• Scam Alert. Members are reminded to NOT send money to buy anything. Don't buy things remote and have it shipped - go get it yourself, pay in person, and take your equipment with you. Scammers have burned people on this forum. Urgency, secrecy, excuses, selling for friend, newish members, FUD, are RED FLAGS. A video conference call is not adequate assurance. Face to face interactions are required. Please report suspicions to the forum admins. Stay Safe - anyone can get scammed.

Ian's Bridgeport mill

According to https://www.inchcalculator.com/horsepower-to-kva-calculator/ the 5kVA transformer should easily handle the 1HP 3 phase motor on my mill?

I think perhaps you missed the nuances of my comment. Although the transformer might be sized and rated for this task. The wiring may not be. To be more clear, the amperage on the low voltage side will be inversely proportional the voltage ratio. If the wires and terminals on the low voltage side are not sized for the current required on the low voltage side to generate the output power for the mill on the high voltage side, they will be seriously compromised.

It seems very odd to me to think that the transformer was sized that big though. I can't appreciate that there was any need for that. It seems more like an over designed system assembled by someone who didn't really know what they were doing and chose to err on the safe side or perhaps even more likely by someone who did know what they were doing but chose to use what was available rather than to buy and use ideal components. We might never know.

In any event, I can't really see any advantage to using the transformer to step up the voltage from 120 or 220 to 575. To do so will require 120 or 220 3 pH and careful analysis of the wiring limits as described earlier. Also, to be very clear, the 3phase output of a VFD is not a suitable input for any transformer. At a minimum, transformer influenced feedback to the VFD will be misinterpreted to the detriment of VFD output voltage control and at worst could result in serious damage to the VFD circuits.

On the other hand, using the transformer to generate single phase low voltage output to power other devices such as DROs and power feeds would work quite well and given that they exist on the subject machine I am reasonably confident that this is how the transformer was used - albeit overdesigned.

Without detailed knowledge of the previous usage of the system all of the above is just educated speculation on my part.
 
It comes down to power consumption basically forget losses for the moment, consider watts required. This is basically V x A = Watts used. So as the voltage goes lower the amps increase. This is where you tun into trouble increased amperage requires increased conductor size.

Now as to VFD conversions here is done through a little electronic switching magic transformation (same power Watts).

Now using a transformer in the system with a VFD adds another complexity of induction that must be neutralized to keep the electronics happy.

It is likely less costly to get the motor rewound or replaced with something to match (or closely match) your existing supply.
 
I think perhaps you missed the nuances of my comment. Although the transformer might be sized and rated for this task. The wiring may not be. To be more clear, the amperage on the low voltage side will be inversely proportional the voltage ratio. If the wires and terminals on the low voltage side are not sized for the current required on the low voltage side to generate the output power for the mill on the high voltage side, they will be seriously compromised.

It seems very odd to me to think that the transformer was sized that big though. I can't appreciate that there was any need for that. It seems more like an over designed system assembled by someone who didn't really know what they were doing and chose to err on the safe side or perhaps even more likely by someone who did know what they were doing but chose to use what was available rather than to buy and use ideal components. We might never know.

In any event, I can't really see any advantage to using the transformer to step up the voltage from 120 or 220 to 575. To do so will require 120 or 220 3 pH and careful analysis of the wiring limits as described earlier. Also, to be very clear, the 3phase output of a VFD is not a suitable input for any transformer. At a minimum, transformer influenced feedback to the VFD will be misinterpreted to the detriment of VFD output voltage control and at worst could result in serious damage to the VFD circuits.

On the other hand, using the transformer to generate single phase low voltage output to power other devices such as DROs and power feeds would work quite well and given that they exist on the subject machine I am reasonably confident that this is how the transformer was used - albeit overdesigned.

Without detailed knowledge of the previous usage of the system all of the above is just educated speculation on my part.

My intended point was that if I went the RPC route the transformer was already here making that option more attractive. I wasn't planning on using the transformer for anything else, at least not yet. Presumably modding former output wires to appropriate capacity as input wires would not be a big problem. I suppose a 5kVA transformer might be as small as they get in an industrial shop but in my shop there's only myself at work and I've never used two machines at once. The mill I think is a relatively small Bridgeport and not a big juice consumer. Probably perfect for my small shop though.
 