Now I'm confused! I'll credit it to being tired - I'm over 20 hours up right now. I have a faint impression it is inrush current caused by induction, but I'll have to sleep on this. For the moment I've stricken the assertion, and I'm going to bed.
I don't understand. It's an over-simplication, I know, but can't I think of the windings as resistors? If the voltage is halved, won't the current be halved, not doubled?
A few weeks ago I mentioned that my scrappie had some suitable 45kva (GO BIG!) transformers for cheap. Where are you?Well, you can use a motor +/- 20% of rated voltage.If the voltage is half, due to lower inductance and lower resistance, the current more than doubles. This results in very fast heating of the windings and insulation failure.
For instance I have a grinder that is 3PH 550V. I can choose a voltage-doubling VFD, but I already have a rotary phase converter and 2 VFDs. I'm looking for an inexpensive 15000 VA 3ph 2:1 transformer instead. If I run it on raw 240V 3PH, I'll smell the magic smoke.
Or double the work at the same voltage?When looking at V=IR in a motor people often forget that the R term includes the work being done. That work is measured as power, and if you need the same power output at lower voltage you have to crank up the amperage.
Yes, and if you think about it you realize that doubling the expected work - imagine adding so much more weight on your spindle to bring up to speed - would take more current and so make a ton more heat.Or double the work at the same voltage?
So, would running a motor at half voltage and no load or much lower-than-rated-load still result in much higher current, overheating, etc... ?Yes, and if you think about it you realize that doubling the expected work - imagine adding so much more weight on your spindle to bring up to speed - would take more current and so make a ton more heat.
That I can't answer. I suspect that the motor internals are unlikely to like it because of all the various inductance issues that go on, but you'd have a much higher chance of not burning it out.So, would running a motor at half voltage and no load or much lower-than-rated-load still result in much higher current, overheating, etc... ?
While we are talking about what you can and can't get away with in single and 3 phase motors, I have found that some things out of spec are tolerated and other things aren't. This was based on 3 and 5 hp 220v motors From my experience over the years, you can run a 50hz (single ph) motor on 60hz and it works fine. The other way (60hz motor on 50hz) the motor overheats under load.So, would running a motor at half voltage and no load or much lower-than-rated-load still result in much higher current, overheating, etc... ?
Most of the explanations seem to assume that the load is constant as the voltage is reduced - basically requiring the same power from the motor while supplying half the voltage in our example. So obviously the current must increase. Lots of explanations online use terms like the motor 'trying' or 'wanting' to do something, which is interesting.
So, would running a motor at half voltage and no load or much lower-than-rated-load still result in much higher current, overheating, etc... ?
Yes, but you seem to be saying that the motor will draw the same current at no load, as with its maximum load: "If it takes a quarter hp to turn at motor at its 60hz speed, it takes a 1/4 hp period."I think what you are missing here is the fact that the rated hp is the MAXIMUM the motor can do safely. But the rated hp is only reached when the load hp equals the motors rated HP. This is rarely the case. Usually, motors run at much less than their rated hp. It's a. Big mistake to assume that a 2Hp motor produces 2Hp all the time.
I cannot say from the plate alone.Would this motor be a good candidate?
From personal experience and being told this by and industrial sparky: A 3ph motor can run 20% over or under the voltage on the nameplate and not be harmed. But because of the issues stated by Dabbler, that the motor wants to see watts and will get it the hard way if voltage is lowered, I have always made it a habit to double the HP of the motor I was replacing if I was running off a VFD motor. It is much easier on the motor at low rpm and heat is hard to detect. If you are putting a 5hp in place of a single phase 1.5HP that motor has an easy life.While we are talking about what you can and can't get away with in single and 3 phase motors, I have found that some things out of spec are tolerated and other things aren't. This was based on 3 and 5 hp 220v motors From my experience over the years, you can run a 50hz (single ph) motor on 60hz and it works fine. The other way (60hz motor on 50hz) the motor overheats under load.
If the voltage on one leg of the three phases is low, that set of windings will overheat and burn out.
Also, a note of caution. The fan is designed to adequately cool the motor at the nameplate rpm. If you are running with a load on your lathe at low rpm using a VFD, you might want to provide alternate cooling for the motor because it's fan is not turning fast enough to keep up with the heat.
Chris
If you are putting a 5hp in place of a single phase 1.5HP that motor has an easy life.
Thanks guys! The discussion has been most helpful. I now know what I am looking for. I am willing to take the time to get something that checks all the boxes. I’ve also been doing my own research online and understand better what’s involved.@Ironman That is why I suggest 1 HP more on a lathe. Sure 2HP more is better, but then the motor frame is so big it sometimes just won't fit.
A best practice is the largest frame that will fit (within reason). The biggest trouble in fitting a three phase motor is getting the frame to fit with enough horsepower to do the job.
*Note* I always replace a mill motor with the same HP rating - there isn't a lot of advantage to overpower a mill. But it makes installation a pain if the motor is much bigger and heavier. Particularly if the motor mounts are marginal.