I was looking at my VFD Output Voltage Characteristics on an oscilloscope recently and noticed some very high harmonic spikes. The spikes are not surprising - in fact expected given the square wave characteristics of the VFD output voltage. But I didn't expect voltage level spikes over 2000 volts.
So I sent an Email to TECO - the manufacturer of my VFD to ask about it. Rather than reply to my email, they called me.
The fellow said such spikes were typical of short cable runs between the VFD and the motor and especially in higher quality motors such as inverter ready motors like I have because they don't dampen the spikes and instead are designed to tolerate them. I'm not really surprised by any of that either. It's really just the very high voltage levels that surprised me.
But what he said next totally caught me off gaurd. He recommended 3 phase OUTPUT filtering! At first, I was stunned. I have always assumed that the VFD measures current flow and back EMF from the motor and uses that information to set output parameters to optimize motor performance. He didn't disagree. However, he said that designing a filter with a cutoff frequency at least twice the carrier frequency would kill the spikes but still allow the current flow at the carrier frequency voltage to reach the analytical portion of the sensorless vector circuitry in the VFD.
So that's what I plan to do. I guess we will see how well that works.
I'm also curious to know if anyone else has had similar experiences or has tried output filtering. Please note that this is not input filtering on the single phase input circuit which is very common and in fact I am already doing that. This is output filtering on the 3 phase power from the VFD to the motor.
So I sent an Email to TECO - the manufacturer of my VFD to ask about it. Rather than reply to my email, they called me.
The fellow said such spikes were typical of short cable runs between the VFD and the motor and especially in higher quality motors such as inverter ready motors like I have because they don't dampen the spikes and instead are designed to tolerate them. I'm not really surprised by any of that either. It's really just the very high voltage levels that surprised me.
But what he said next totally caught me off gaurd. He recommended 3 phase OUTPUT filtering! At first, I was stunned. I have always assumed that the VFD measures current flow and back EMF from the motor and uses that information to set output parameters to optimize motor performance. He didn't disagree. However, he said that designing a filter with a cutoff frequency at least twice the carrier frequency would kill the spikes but still allow the current flow at the carrier frequency voltage to reach the analytical portion of the sensorless vector circuitry in the VFD.
So that's what I plan to do. I guess we will see how well that works.
I'm also curious to know if anyone else has had similar experiences or has tried output filtering. Please note that this is not input filtering on the single phase input circuit which is very common and in fact I am already doing that. This is output filtering on the 3 phase power from the VFD to the motor.