Over on another thread Tom Kitta said:
I thought I'd reply in a separate thread since I can see this discussion going off in its own direction.
I have not yet tried my VFD, although the person I got it from (my cousin) tested it and it apparently works.
To answer some of the above questions, you first need to think a bit about how VFD's work.
The first stage in all of them is to rectify the AC input into DC. That is called the DC bus on the VFD. That is done with sets of diodes. To full-wave rectify 3-phase power you use 6 diodes (two on each phase). To rectify single phase (aka split phase) power you use 4 diodes - again 2 per phase.
Most 3-phase input VFD's do not care if you only feed two of the three input phases. Some VFD's will generate an error code if the third phase is not powered. That is really just a diagnostic feature to warn you that one of the input phases is missing. Those VFD's can generally be fooled when being fed single phase power by connecting one input to phase A, and the other to phase B and C. All the VFD is really doing is checking that there is power at each input, not that it is really valid 3-phase power separated by 120 degrees instead of 180 degrees.
The bottom line is that the AC input will be rectified and feed the DC bus regardless of whether it is 3 phase or single phase.
There are some limitations though. If fed 3-ph power, the load is spread across the 6 input diodes instead of just 4 when it is fed single phase. If you connect one of the single phase inputs to two input phases on a 3ph VFD, you help reduce the stress on the four diodes that are doing half the work, but the remaining 2 are still doing half the work instead of a third.
The input diodes are the first reason you need to de-rate a 3-ph VFD when fed single phase power. The input diodes are not really big power wasters, and since big diodes are relatively easy and cheap to make they are usually oversized anyway, so although you should de-rate a bit based on the input diodes, it is not really that critical.
Next is the issue that the three phases of 3-ph power are staggered by 120 electrical degrees, while with single phase, the two lines are separated by 180 electrical degrees. That means that with single phase power there is an AC peak 120 times a second (based on a 60 hz AC frequency). With 3-ph the peaks come 180 times a second. In other words, the DC bus is "recharged" every 5.6 milliseconds (1/180) with 3-ph, and only every 8.3 ms (1/120) with single phase.
The next thing to understand about the DC bus is that is is backed up by a capacitor bank that charges when there is an AC peak, and discharges between the peaks. With the peaks being further apart with a single phase input, the DC bus voltage will sag more between AC peaks, and need more current to charge up again when the peak does occur. This is the biggest reason that you must de-rate a 3-ph VFD when it is being fed single phase power. The pulsing of the DC bus causes additional AC currents in the DC bus capacitors, which are the real limiting factor.
The DC bus runs at pretty high voltages. With 240V single phase input, the DC bus will run at around 340V DC. That is 1.4 (square root of 2 actually) times 240. With 208V 3-ph, the bus will run at 208 x 1.4 = 291 V DC. The bus us usually designed to handle around 400VDC on a 240/208V VFD.
The engineers have done the math on this and the magic de-rating number is 1.73. That means that the VFD will draw 1.73 times the current when being fed single phase instead of three phase power. So, if your 3-ph motor has a current rating of 14A, the VFD will need to be able to handle about 24A from a single phase source. Or, conversely, if the VFD is rated for 21A, when fed with single phase power, it can only properly drive a motor rated at 12A.
Most VFD's can handle short overloads of 1.5-2.0 times the average current, so there is some headroom for peak currents caused during startup and intermittent heavy loads - usually peaks loads for less than a couple of seconds.
Most VFDs are pretty durable beasts. They are micro-controller controlled and the CPU regularly monitors all sorts of things (temperatures, currents, and voltages) and will almost always shut the VFD down before anything happens to let out the magic smoke.
Note that all I have talked about is how the DC bus is fed from the input power. That is all that really matters. The back end of the VFD works identically no matter how the DC bus is fed. The back end chops the DC bus at a very high frequency (usually 8-20KHz) to produce an AC current at the desired voltage and frequency. There are three chopping circuits, that produce a signal that offset by 120 electrical degrees so three phases are generated.
Sorry, I know this is all pretty complicated, but hopefully this explanation will help. Ask questions and i will try to answer them as well as I can.
Quick question about VFD - how does the 5hp VFD work on your lathe - have you tried it yet? I know there is a lot of talk about "some" VFDs having issues with single phase input as they are using 4 out of 6 inputs & there is some talk about de-rating VFDs.... not sure whatever this deals with people simply wanting bigger.
Other thread talks about 3hp VFD being able to start 50hp motor over 20-30 seconds...
With a lathe it seems the startup is critical as the chuck is heavy - not so with a mill.
Yet other people talk about how it is not possible to run multiple motors on a VFD - while other people compute the VFD power needed just to do that.
Great work on the lathe BTW - I see how much I have to do to restore my old K&T 2E - she is older than my dad. So far the mill head and gears were in as new condition.
I thought I'd reply in a separate thread since I can see this discussion going off in its own direction.
I have not yet tried my VFD, although the person I got it from (my cousin) tested it and it apparently works.
To answer some of the above questions, you first need to think a bit about how VFD's work.
The first stage in all of them is to rectify the AC input into DC. That is called the DC bus on the VFD. That is done with sets of diodes. To full-wave rectify 3-phase power you use 6 diodes (two on each phase). To rectify single phase (aka split phase) power you use 4 diodes - again 2 per phase.
Most 3-phase input VFD's do not care if you only feed two of the three input phases. Some VFD's will generate an error code if the third phase is not powered. That is really just a diagnostic feature to warn you that one of the input phases is missing. Those VFD's can generally be fooled when being fed single phase power by connecting one input to phase A, and the other to phase B and C. All the VFD is really doing is checking that there is power at each input, not that it is really valid 3-phase power separated by 120 degrees instead of 180 degrees.
The bottom line is that the AC input will be rectified and feed the DC bus regardless of whether it is 3 phase or single phase.
There are some limitations though. If fed 3-ph power, the load is spread across the 6 input diodes instead of just 4 when it is fed single phase. If you connect one of the single phase inputs to two input phases on a 3ph VFD, you help reduce the stress on the four diodes that are doing half the work, but the remaining 2 are still doing half the work instead of a third.
The input diodes are the first reason you need to de-rate a 3-ph VFD when fed single phase power. The input diodes are not really big power wasters, and since big diodes are relatively easy and cheap to make they are usually oversized anyway, so although you should de-rate a bit based on the input diodes, it is not really that critical.
Next is the issue that the three phases of 3-ph power are staggered by 120 electrical degrees, while with single phase, the two lines are separated by 180 electrical degrees. That means that with single phase power there is an AC peak 120 times a second (based on a 60 hz AC frequency). With 3-ph the peaks come 180 times a second. In other words, the DC bus is "recharged" every 5.6 milliseconds (1/180) with 3-ph, and only every 8.3 ms (1/120) with single phase.
The next thing to understand about the DC bus is that is is backed up by a capacitor bank that charges when there is an AC peak, and discharges between the peaks. With the peaks being further apart with a single phase input, the DC bus voltage will sag more between AC peaks, and need more current to charge up again when the peak does occur. This is the biggest reason that you must de-rate a 3-ph VFD when it is being fed single phase power. The pulsing of the DC bus causes additional AC currents in the DC bus capacitors, which are the real limiting factor.
The DC bus runs at pretty high voltages. With 240V single phase input, the DC bus will run at around 340V DC. That is 1.4 (square root of 2 actually) times 240. With 208V 3-ph, the bus will run at 208 x 1.4 = 291 V DC. The bus us usually designed to handle around 400VDC on a 240/208V VFD.
The engineers have done the math on this and the magic de-rating number is 1.73. That means that the VFD will draw 1.73 times the current when being fed single phase instead of three phase power. So, if your 3-ph motor has a current rating of 14A, the VFD will need to be able to handle about 24A from a single phase source. Or, conversely, if the VFD is rated for 21A, when fed with single phase power, it can only properly drive a motor rated at 12A.
Most VFD's can handle short overloads of 1.5-2.0 times the average current, so there is some headroom for peak currents caused during startup and intermittent heavy loads - usually peaks loads for less than a couple of seconds.
Most VFDs are pretty durable beasts. They are micro-controller controlled and the CPU regularly monitors all sorts of things (temperatures, currents, and voltages) and will almost always shut the VFD down before anything happens to let out the magic smoke.
Note that all I have talked about is how the DC bus is fed from the input power. That is all that really matters. The back end of the VFD works identically no matter how the DC bus is fed. The back end chops the DC bus at a very high frequency (usually 8-20KHz) to produce an AC current at the desired voltage and frequency. There are three chopping circuits, that produce a signal that offset by 120 electrical degrees so three phases are generated.
Sorry, I know this is all pretty complicated, but hopefully this explanation will help. Ask questions and i will try to answer them as well as I can.