I was out by my devoted snowblower shed today. I also use the shed to hang my longer metal stock from the roof. I was looking at my Honda HSS724ACTD and HS720CC and thinking what I need to do to get ready for the season. Last year I was debating whether to sell the two stage 724 this spring, but now glad I didn't.
While looking at my ladies, I heard my Lennox Air Conditioner making an odd sound. Went inside the house: blower in furnace OK. Evaporator coil not frozen, only warm air from register though. When I cycled unit on and off I noticed condenser fan wasn't spinning, but would spin if kick-started.
Went to local parts dealer and picked up new start/run capacitor for $54. Runs like a dream now.
Years ago my neighbour had a similar problem but didn't address it soon enough. The thermal overload eventually failed in the compressor and it cost him almost $2000 for repairs.
I'm sure in the next day or two I would have noticed the house temp not falling and investigated. But catching it so soon may have helped.
While looking at my ladies, I heard my Lennox Air Conditioner making an odd sound. Went inside the house: blower in furnace OK. Evaporator coil not frozen, only warm air from register though. When I cycled unit on and off I noticed condenser fan wasn't spinning, but would spin if kick-started.
Went to local parts dealer and picked up new start/run capacitor for $54. Runs like a dream now.
Years ago my neighbour had a similar problem but didn't address it soon enough. The thermal overload eventually failed in the compressor and it cost him almost $2000 for repairs.
I'm sure in the next day or two I would have noticed the house temp not falling and investigated. But catching it so soon may have helped.