I‘ve had my electric shop heater since the fall of 2021. Yesterday I noticed that the fan was running continuously - even when the heating elements were off.
Heater Details:
Thermo Sphere Heavy Electric Utility Heater
Model: EH-4610
Here is the data plate:
It was bought at PA and has been working well. Investigation showed that the Motor Delay Relay (MDR) has its contacts closed continuously because the capillary tube has a pin hole in it and all the liquid escaped.
The relay is basically a temperature sensing device between the fins. When the thermostat calls for heat, the heater coil relay closes and the resistive elements start heating up. When a certain temperature is reached, the fan motor is turned on by the MDR. When the thermostat pre-set temperature is reached, the heater coil relay cuts out the resistive heating elements, but the fins are still hot. The fan motor keeps running until they are cooled below a certain temp, again sensed by the MDR which then opens its contacts and shuts the fan off.
The capillary tube of the MDR is installed as such (fins pried open for removal and visibility)
The tube was bent incorrectly at installation in the factory and rubbed on the rear of one of the fins. Since I “opened” the fins in the front, there is clearance - as shown in the picture. There was not when the fins were bent shut to capture the capillary.
The MDR
And an image of the pin hole
Here is the data on the MDR
Here is the website of the manufacturer and specifications of the MDR
I contacted the Service email and Tech Support in Boucherville, QC, they have no parts and can’t get any either.
I am asking for help finding either a direct replacement or something equivalent.
Or can the capillary tube be repaired (I think I can solder the pin hole shut) and liquid (I think there is alcohol in those tubes) put back in? Has anyone successfully repaired something like this?
For now I have wired the fan motor to an auxiliary contact on the heater coil contactor. Fan runs when resistive heaters are on (as controlled by the thermostat). My worry is that the elements will burn out prematurely as they are not fan cooled upon shutdown - this is what the MDR is for.
Thanks in advance for your time.
Heater Details:
Thermo Sphere Heavy Electric Utility Heater
Model: EH-4610
Here is the data plate:
It was bought at PA and has been working well. Investigation showed that the Motor Delay Relay (MDR) has its contacts closed continuously because the capillary tube has a pin hole in it and all the liquid escaped.
The relay is basically a temperature sensing device between the fins. When the thermostat calls for heat, the heater coil relay closes and the resistive elements start heating up. When a certain temperature is reached, the fan motor is turned on by the MDR. When the thermostat pre-set temperature is reached, the heater coil relay cuts out the resistive heating elements, but the fins are still hot. The fan motor keeps running until they are cooled below a certain temp, again sensed by the MDR which then opens its contacts and shuts the fan off.
The capillary tube of the MDR is installed as such (fins pried open for removal and visibility)
The tube was bent incorrectly at installation in the factory and rubbed on the rear of one of the fins. Since I “opened” the fins in the front, there is clearance - as shown in the picture. There was not when the fins were bent shut to capture the capillary.
The MDR
And an image of the pin hole
Here is the data on the MDR
Here is the website of the manufacturer and specifications of the MDR
AuOne Electrical Co., Ltd
www.auone.com
I contacted the Service email and Tech Support in Boucherville, QC, they have no parts and can’t get any either.
I am asking for help finding either a direct replacement or something equivalent.
Or can the capillary tube be repaired (I think I can solder the pin hole shut) and liquid (I think there is alcohol in those tubes) put back in? Has anyone successfully repaired something like this?
For now I have wired the fan motor to an auxiliary contact on the heater coil contactor. Fan runs when resistive heaters are on (as controlled by the thermostat). My worry is that the elements will burn out prematurely as they are not fan cooled upon shutdown - this is what the MDR is for.
Thanks in advance for your time.