• Scam Alert. Members are reminded to NOT send money to buy anything. Don't buy things remote and have it shipped - go get it yourself, pay in person, and take your equipment with you. Scammers have burned people on this forum. Urgency, secrecy, excuses, selling for friend, newish members, FUD, are RED FLAGS. A video conference call is not adequate assurance. Face to face interactions are required. Please report suspicions to the forum admins. Stay Safe - anyone can get scammed.

Finally: 3 Phase Power With A 10 HP Rotary Phase Converter

RobinHood

Ultra Member
Premium Member
With 8 3 phase motors in the shop, it was time to come up with a better way to run the motors other than with two VFDs (which were connected to the motor that I was about to use and then swapped to the next motor) --> welcome the RPC. I bought an used one from a colleague that was powering an air compressor, but had not been used for about 2 years. It was a very basic unit with no motor/circuit protection and was not operational when I got it. I repaired it, but knew it needed a "facelift".

Here it is as I bought it
IMG_0581.JPG

It gave me the basic components: idler motor, start capacitors, run capacitors, and differential voltage relay. I found an used motor contactor / overload protection and a much bigger cabinet; also, some switches and control lights. I did have an old contactor with a 575V coil - which was replaced with a 240V coil. I had a lot of #10 AWG wire, terminal ends, and a bunch of time...

Here is what the new set-up looks like. The red light indicates that there is power to the unit, but it is not running
IMG_0586.JPG

With the RPC running, the red light is out, the green light is on (plus one can hear the idler motor of course, although it is surprisingly quiet!)
IMG_0587.JPG

Here is the inside
IMG_0588.JPG
On the door we have the back ends of the switches and control lights. In the box, bottom left, is the main contactor / motor overload relay. Above it are the run caps. Top right are the start caps. Below them is the start contactor, with the differential voltage relay for control, just below it. In the lower centre are the bus bars. All feeds to/from the RPC are from the bottom.

Here is a closer view
IMG_0589.JPG

This is the schematic I came up with - based on designs found on PracticalMachinist.com and other sources; (yes, I did use a trial version of a circuit drafting software...)
IMG_0590.JPG

Some of the performance numbers while the RPC is running under no load:
VL1L2 = Vab: 246.1 VAC
Vac: 255.6 VAC
Vbc: 257.6 VAC
IL1L2 = Iab: 5.1 A
Iac: 15.3 A
Ibc: 12.9 A
Cab: 150 MFD
Cbc: 90 MFD
Cstart: 700 MFD
Cpf: not used

With a ~ 2.5hp motor load, Vac and Vbc drop closer to the line voltage (Vab) and the currents Iac and Ibc go up, but start to equalize. Line current increases to about 11.0 A.

How I built this unit is based on what I had on had / was able to source locally. By no means is it the only way to build a RPC.

In conclusion, the RPC project was successful and I am looking forward to run my machines with it...
 
Last edited:
There will probably one of those in my near future for the transformer to power the lathe my son says they were running it on 220 but I think it will be 3 phase.
 
Hello RobinHood, I was just looking over your RPC setup and wondering how it has been working? Have you had any issues with the potential relay?
 
No problems whatsoever. Seems much easier on the pony motor as it just spins down under it’s own inertia until the rotor runs out of energy - which takes quite a while!

Incidentally, I have since bought a commercially made 7.5hp RPC. They also do not disable the potential relay on shut down (like on the original 10hp design I describe above before the mod). So, after power is cut, the pony motor free wheels for a bit until the potential relay kicks in again and then abruptly stops the rotor. I am sure it does not physically hurt the electric motor, but I am not sure about the electrics as it is the back emf that is generating the magnetic field in an otherwise unpowered system. Also don’t know if it would affect the longevity of the caps. Most likely going to put a cut-out relay in it as well so that the potential switch is cut out after start-up and stays that way until the next start - like I did to the 10hp RPC.
 
Good to hear, I am considering going with either a potential or a zero crossing relay and just weighing the options.
It sounds like it is using the generated voltage as a brake. You could probably change the set point on the relay to a lower setting if you thought it was doing any harm to the motor. I agree with you about the back emf and it quickly collapsing when the relay is closed.
 